Rescale the temperature bar. Right click, Dialogs, File/Data/Coloring |
Beta Was this translation helpful? Give feedback.
-
Even after rescaling the colorbar you will not see an exact match, but it should be close. This is for a few reasons: -Slice files write instanteneous data. Devices write data averaged over the output interval. |
Beta Was this translation helpful? Give feedback.
-
The contour image you have in your first post is not from Smokeview and appears to be the Pyrosim native viewer. Do you see the same thing if you use Smokeview? |
Beta Was this translation helpful? Give feedback.
-
I ran your input file from your first post with the current release. |
Beta Was this translation helpful? Give feedback.
-
I think the defaults bounds in Pyrosim are not max/min but certain percentage. Try choosing the different settings in scale bar settings. |
Beta Was this translation helpful? Give feedback.
-
I am simulating a model in FDS and while populating the results for temperature 3d plot, the max temperature visible in the results is approx. 400 deg compared to the temperature recorded by the devices at the same location i.e is 1200 deg. I am attaching the FDS file along with the screen shot of the 3d plot and device result. The location of the THCP device is at the surface of the fire block. Kindly suggest remedial measures.
T1.zip
Beta Was this translation helpful? Give feedback.